STEP Warmfloor™ Online Support => Technical Support / Installation => Topic started by: cfasnacht on January 10, 2008, 11:40:33 AM



Title: Transformer noise and heat
Post by: cfasnacht on January 10, 2008, 11:40:33 AM
Good morning,

customer installed a SYS120 system and in concerned with the amount of noise and heat being generated by the transformer. They are using a switch to turn the power on and off.
    Can you give me an idea of what might be causing the issues.

Regards,

Chris Fasnacht
Minnesota Electric
(612) 804-4305


Title: Re: Transformer noise and heat
Post by: bbillhartz on January 15, 2008, 11:38:13 AM
Good morning.

The transformer used for the SYS-120 kit is a 1000 watt transformer.  Can you tell me where and how the transformer is installed?

It is completely normal for transformers in operation to have a surface temperature between 158 and 176 degrees Fahrenheit (70-80 degrees Celcius).  Also, do not place the transformer in an area where the ambient temperature is higher than 104 degrees Fahrenheit (40 degrees Celcius).

Also, is the noise caused by vibration?  Good mounting points are concrete pillars, brick walls, steel girders, and wooden beams.  Rubber standoffs (between the mounting holes of the transformer and the mounting surface) will reduce vibration as well.

I hope this helps.  Give our technical support a call for more suggestions and ideas to your problem, toll-free at 877-783-7832.