I'm an engineer working on the remodel of an existing custom home. One large room of the home has a Warmfloor system with a Digi-Lux thermostat. The room is also served by a forced-air cooling system. Currently, there is no coordination between heating and cooling in the room.

To prevent simultaneous heating and cooling, can we intercept the white wire (V-) from the thermostat to the regulator to disable the Warmfloor heating when the room is in cooling mode? If not, what's the best way to accomplish this?

Thanks for your help.
Logged
Tim
Technical Support
Newbie
*****
Posts: 17


View Profile
« Reply #1 on: March 13, 2008, 03:14:08 PM »

Interrupting the V- would not just turn off the power to the transformer, but the display on the thermostat as well; so that would work.

If, on the other hand, you interrupt the trig, the triac won't let power go to the transformer but the display on the thermostat would still stay on.
Logged
 
Pages: [1]
  Print  
 
Jump to:  

Powered by SMF 1.1.2 | SMF © 2006-2007, Simple Machines LLC

Getting Started

Did You Know?

Indoor Air Quality is directly correlated with respiratory illness.  The last thing you want your mechanical system to do is to distribute dust, mold spores, pollen, and other particulates throughout the structure. Because radiant heat does not blow allergens, it helps those with allergies and asthma find dramatic improvement to their symptoms.