I have installed the StepWarm product in my bathroom. After everything is hooked up and I have tiled over the elements. The tile is warming up, however, it is very uneven. Any reason why and any possible resolutions?

-mark
Logged
Tim
Technical Support
Newbie
*****
Posts: 22


View Profile
« Reply #1 on: January 07, 2008, 08:31:20 AM »

A few different things that may be the problem.  The first thing I'd check is amperage on each element to be sure they're all well connected.  Our standard residential elements (EP-30-2-24V-24W) should be around .325 amps per foot at 24 volts.  If your meter says something different, you may have a connection problem.

If it turns out that you don't have a connection problem, then perhaps you need some/ some more insulation below the elements, or make sure your insulation is properly installed.  If you have access to joist cavities below the Warmfloor installation, you can put fiberglass insulation up against the bottom of the subfloor (being sure that you don't leave an air gap between the insulation and the botom of the subfloor.)

And if you don't think these suggestions are relevent, then you should probably call our tech help line (1-877-783-7832).
Logged
 
Pages: [1]
  Print  
 
Jump to:  

Powered by SMF 1.1.2 | SMF © 2006-2007, Simple Machines LLC

Getting Started

Did You Know?

Studies from the "Sick Building Syndrome" show a direct relation between indoor climate and symptoms such as fatigue and headaches.  Research shows that thermic indoor climate is also related to productivity.  The level of comfort with radiant heat at lower temperatures increases productivity by 20-30%.